Roof Air keeps tripping the circuit breaker
« on: June 20, 2017, 11:34:41 AM »
 HI everyone,
 My wife and I just recently purchased a 2014 Winnie 27N from a private owner with 15000 miles. Unit is like new although we are having problems with the Roof Air conditioner.On real hot days, it runs for about 10 minutes then trips the circuit breaker at the foot of the bed console. We noticed on a cooler day it ran about 1/2 hour then tripped again. I took off the cover to the unit on the roof and there was no filter near the coils. Could it be the coils need to be blown off with high pressure air hose ? HELP.
 I have also noticed that the engine,Triton V10, is lunging or surging going up hills in the lower gears. About every second or so the rpm's jump 200 or so then back and forth. Could it be bad gas and a new fuel filter is needed?
 We are new at rving since the pop up 20 years ago so we are not familiar with this unit. Any suggestions are welcome.
 Thanks

Greg E.

edit by staff - changed message icon to topic solved
« Last Edit: July 06, 2017, 07:19:44 AM by John Canfield »

John Canfield

  • Forum Staff
  • ---
  • *
  • Posts: 11942
    • Jane and John's Internet Home
Re: Roof Air keeps tripping the circuit breaker
« Reply #1 on: June 20, 2017, 06:17:46 PM »
Hi Greg,

The A/C problem sounds like either a bad run capacitor (on the roof air) or the circuit breaker in your Winnie's load center.

Please start a new topic about the engine issue in the Motorhome board or General Discussion board.
--John
2005 Horizon 40AD, 2006 Jeep Rubicon Unlimited
Our Horizon projects
Our weather

lavarock1210

  • ---
  • Posts: 378
Re: Roof Air keeps tripping the circuit breaker
« Reply #2 on: June 20, 2017, 06:59:22 PM »
If we were to know what brand and size the AC is will help.

Also what size is the circuit breaker?

I assume this is when on shore power.

What is the voltage when the AC is running?

Greg E.

  • ---
  • Posts: 15
Re: Roof Air keeps tripping the circuit breaker
« Reply #3 on: June 21, 2017, 08:16:30 AM »
 Yes this is on shore power. I'm not that knowledgeable about the other things you asked about. The unit is not stored at my home, so I will look this weekend. Thanks for your response.

John Canfield

  • Forum Staff
  • ---
  • *
  • Posts: 11942
    • Jane and John's Internet Home
Re: Roof Air keeps tripping the circuit breaker
« Reply #4 on: June 21, 2017, 11:45:32 AM »
Then it sounds like you are going to need some technical assistance. An AC tech can use a clamp-on ammeter to see how much current the roof air is drawing - if too much then the run capacitor could be bad (or maybe something else in the roof unit itself). If the current is nominal, then the breaker in your load center is suspect (assuming shore power is at/about 110-120v.)
--John
2005 Horizon 40AD, 2006 Jeep Rubicon Unlimited
Our Horizon projects
Our weather

Greg E.

  • ---
  • Posts: 15
Re: Roof Air keeps tripping the circuit breaker
« Reply #5 on: June 27, 2017, 08:11:52 AM »
 Thanks John,
 This weekend we tried to run it off the battery and the generator. Ran for two hours like this and came up to temp. set on the thermostat. Then we tried it while shutting off the generator. The air unit shut off as soon as I shut off the generator. I restarted the generator and the air unit started back up. I think you are right that the unit is drawing too much current. I did notice some Styrofoam up inside on the coils from the surrounding pieces of Styrofoam in the unit. I will try to get a vacuum nozzle up into that area and clean the coils. Hopefully, this will increase the air flow and stop drawing so much current.

John Canfield

  • Forum Staff
  • ---
  • *
  • Posts: 11942
    • Jane and John's Internet Home
Re: Roof Air keeps tripping the circuit breaker
« Reply #6 on: June 27, 2017, 08:33:08 AM »
Oh yes, make sure the coils are clean, I thought with a three year-old unit they would be clean.
--John
2005 Horizon 40AD, 2006 Jeep Rubicon Unlimited
Our Horizon projects
Our weather

TonyDtorch

  • ---
  • Posts: 2203
Re: Roof Air keeps tripping the circuit breaker
« Reply #7 on: June 27, 2017, 01:21:26 PM »
Put a volt meter into a wall socket of the motorhome and check the input 120 volt a/c voltage when it is under start-up load form the air conditioner,  if it goes down to 106 volts and lower it causes the amperage to go way up often tripping the breakers.

because of line loss and summer time lower grid voltage,  you may not be getting enough shore power current.

do the same test while on generator power and compare the difference in voltage drop.

« Last Edit: June 27, 2017, 01:39:39 PM by TonyDtorch »

John Canfield

  • Forum Staff
  • ---
  • *
  • Posts: 11942
    • Jane and John's Internet Home
Re: Roof Air keeps tripping the circuit breaker
« Reply #8 on: June 27, 2017, 05:39:18 PM »
^^ excellent point ^^
--John
2005 Horizon 40AD, 2006 Jeep Rubicon Unlimited
Our Horizon projects
Our weather

Greg E.

  • ---
  • Posts: 15
Re: Roof Air keeps tripping the circuit breaker
« Reply #9 on: June 28, 2017, 08:03:16 AM »
Thanks. I will check it. That may explain the shore power, but shouldn't the air cond. run off the battery too?

Alfa38User

  • ---
  • Posts: 5947
Re: Roof Air keeps tripping the circuit breaker
« Reply #10 on: June 28, 2017, 09:54:30 AM »
Quote
......but shouldn't the air cond. run off the battery too?


No!!! The batteries (and converters) produce 12V DC power, the air conditioners require 120V AC power from either the plugged in shore power or a generator.
 
Stu
Montréal, Canada 🍁
Snowbird, Naples Florida
Alfa Gold 38 (2000) 5ver (parked!)

"Of course I talk to myself, sometimes I need expert advise!!!"

Greg E.

  • ---
  • Posts: 15
Re: Roof Air keeps tripping the circuit breaker
« Reply #11 on: June 28, 2017, 11:07:14 AM »
Thanks Stu. That will help skinny down the problem.

Greg E.

  • ---
  • Posts: 15
Re: Roof Air keeps tripping the circuit breaker
« Reply #12 on: July 05, 2017, 10:55:27 AM »
 I think we found the problem. A relative was visiting who camped for many years and he felt the extension cord I was using at the house was not large enough. We replaced it with one that was larger and the air ran fine. He suggested to have a 30 amp rated cord if I needed to use one and I will have one made for future needs. Being a newbee, everything is new!! Makes you feel silly when you are shown something like this.

Greg

mikef

  • ---
  • Posts: 236
  • Winnebago Posse
Re: Roof Air keeps tripping the circuit breaker
« Reply #13 on: July 05, 2017, 10:59:34 AM »
Always seems 90% of the time, it's something simple.
1992 Winnebago Chieftain 32'
460 Ford chassis, New long block

John Hilley

  • ---
  • Posts: 1656
Re: Roof Air keeps tripping the circuit breaker
« Reply #14 on: July 05, 2017, 11:33:39 AM »
I think we found the problem. A relative was visiting who camped for many years and he felt the extension cord I was using at the house was not large enough. We replaced it with one that was larger and the air ran fine. He suggested to have a 30 amp rated cord if I needed to use one and I will have one made for future needs. Being a newbee, everything is new!! Makes you feel silly when you are shown something like this.

Greg

Just buy an extension cord made with 10 guage or at a minimum 12 gauge wire. Probably cheaper than making one.
2003 Winnebago Adventurer 38G
1999 Jeep Cherokee Sport
1999 Winnebago Brave 35C
  Handicap Lift & Hospital Bed

John Canfield

  • Forum Staff
  • ---
  • *
  • Posts: 11942
    • Jane and John's Internet Home
Re: Roof Air keeps tripping the circuit breaker
« Reply #15 on: July 06, 2017, 07:13:53 AM »
I think we found the problem. A relative was visiting who camped for many years and he felt the extension cord I was using at the house was not large enough. ..
And TonyDtorch wins the prize for calling this one! Glad you chased the problem down. I would just buy a 30 amp RV cable and use an adapter as required. I always carry one because some special event rallies will set up a portable generator (or whatever) and have a limited number of power pedestals.
--John
2005 Horizon 40AD, 2006 Jeep Rubicon Unlimited
Our Horizon projects
Our weather

Greg E.

  • ---
  • Posts: 15
Re: Roof Air keeps tripping the circuit breaker
« Reply #16 on: July 06, 2017, 08:14:22 AM »
 Thanks to everyone. Great forum. What a wealth of knowledge!

Greg

lavarock1210

  • ---
  • Posts: 378
Re: Roof Air keeps tripping the circuit breaker
« Reply #17 on: July 06, 2017, 11:01:16 AM »
Just buy an extension cord made with 10 guage or at a minimum 12 gauge wire. Probably cheaper than making one.

X2  I was able to find a 10 gauge extension cord at Lowes a few years ago.  It is a little heavy but takes care of the voltage drop problem.

 