Author Topic: Ignorant question about putting a 30A Fuse from controller to batteries  (Read 235 times)

BigSkyTrailerGuy

  • ---
  • Posts: 232
  • Love your country, but fear your government
I just pulled the pin of a couple of 100W Solar panels and a Renogy Wanderer controller. 

They specify a 30A fuse between the controller and the batteries --  But if that cable is 4 AWG (for minimum voltage loss),
doesn't the resistance of an in-line fuse negate our coveted current flow?

Sorry again for the ignorance.

John From Detroit

  • ---
  • Posts: 19793
  • ^My New Home^
    • Diabetics Forum
Re: Ignorant question about putting a 30A Fuse from controller to batteries
« Reply #1 on: September 03, 2017, 07:06:03 AM »
No the fuse is a very short section of small wire. The 4AWG is 100's times longer

The resistance is "per foot" so being as the fuse is like 1" there's not much resistance there.
Nothing adds excitement like something that is none of your business
My Home is where I park it.

QZ

  • ---
  • Posts: 340
Re: Ignorant question about putting a 30A Fuse from controller to batteries
« Reply #2 on: September 03, 2017, 07:31:15 AM »
At 200 watts you will get 12 amps or less. If you push close to 30 amps through the fuse you may see insignificant heating of it. I have experienced it with anl fuses. Gadgets like https://www.amazon.com/dp/B01H3DKGFK?th=1 are a cheap way to protect and give you an easy way to disconnect. The high quality version is this https://www.amazon.com/dp/B004XXOVP0/ref=twister_B01ENZVS7G?_encoding=UTF8&psc=1. You may also want a disconnect between the panels and the controller  because some companies specify disconnecting the panels before disconnecting the battery. Your controller manual may mention it.

Gary RV_Wizard

  • Forum Staff
  • ---
  • *
  • Posts: 61019
  • RVer Emeritus
Re: Ignorant question about putting a 30A Fuse from controller to batteries
« Reply #3 on: September 03, 2017, 09:40:44 AM »
As QZ & John say, your max current flow is nowhere near 30A, so the fuse is insignificant in the circuit resistance. 4 AWG cable is probably way overkill anyway. Even 10 gauge will handle 200 watts (about 12A @ 16v) with insignificant loss, and 10 gauge is rated for 30A loads.
Gary
--------------
Gary Brinck
Summers: Black Mountain, NC
Home: Ocala National Forest, FL

Lou Schneider

  • Forum Staff
  • ---
  • *
  • Posts: 7409
Re: Ignorant question about putting a 30A Fuse from controller to batteries
« Reply #4 on: September 03, 2017, 04:15:51 PM »
How far from the batteries is the solar controller?  Put it close by and the need for overly large wire becomes insignificant.

In any case, you do want a fuse close to the batteries in case you get an internal short in the controller or an external short in the wiring.  Better a fuse gets hot and blows than the wiring gets hot and starts a fire.

sunfighter

  • ---
  • Posts: 46
Re: Ignorant question about putting a 30A Fuse from controller to batteries
« Reply #5 on: September 04, 2017, 08:10:57 AM »
Here's my 30 amp fuse setup. Being an old guy, I used the jumbo size fuse. (easier to see)  :D :D
"Leaning in a heavy wind that no one else can feel"

2007 Gulf stream Independence triple slide. and 2005 Gulf Stream Independence triple slide

AStravelers

  • ---
  • Posts: 693
  • Part time travelers, 4-8 months each year.
Re: Ignorant question about putting a 30A Fuse from controller to batteries
« Reply #6 on: September 07, 2017, 11:26:18 AM »
I would install a Blue Sea 30amp circuit breaker disconnect switch like this: https://www.amazon.com/dp/B0055MV7AA/ref=twister_B01ENZVS7G?_encoding=UTF8&psc=1

This give you the ability to disconnect the controller much easier than pulling the fuse.