Since this is a general question forum, I have an electrical question for the real electricians on here. Today, I installed 5 120v/15 amp receptacles in the pole barn. I?m not licensed, but I?ve done a lot of electrical work here and am comfortable with it and have a pretty good understanding of it.
I installed the receptacles and the last thing I did was install a 20 amp GFCI to protect the downstream receptacles. Turned on the breaker and the GFCI would not reset. Disconnected the load side of the GFCI and left line side hooked up, GFCI reset and held. Tested continuity between positive and the grounds and neutrals and got zero. Continuity between grounds and neutrals tested good. Tried hooking the GFCI back up, would not reset. Unhooked load side again, GFCI reset and held. With the GFCI reset, I used pliers and touched the white neutral wire to the load side neutral screw on the GFCI, the GFCI immediately tripped.
I inspected each receptacle and saw that on one of them, the bare copper ground wire on one of them was touching a neutral screw of one of the receptacles. ( I was using #12 wire so it was tight pushing all those wires into the boxes.) I corrected it so the grounds werent touching anything and now the GFCI is working normally.
If I hadn?t been using a ground fault I?m sure this circuit would have worked fine. I just can?t wrap my head around why the GFCI would trip when the ground wire touched the neutral. It was the third receptacle in series after the ground fault.
I installed the receptacles and the last thing I did was install a 20 amp GFCI to protect the downstream receptacles. Turned on the breaker and the GFCI would not reset. Disconnected the load side of the GFCI and left line side hooked up, GFCI reset and held. Tested continuity between positive and the grounds and neutrals and got zero. Continuity between grounds and neutrals tested good. Tried hooking the GFCI back up, would not reset. Unhooked load side again, GFCI reset and held. With the GFCI reset, I used pliers and touched the white neutral wire to the load side neutral screw on the GFCI, the GFCI immediately tripped.
I inspected each receptacle and saw that on one of them, the bare copper ground wire on one of them was touching a neutral screw of one of the receptacles. ( I was using #12 wire so it was tight pushing all those wires into the boxes.) I corrected it so the grounds werent touching anything and now the GFCI is working normally.
If I hadn?t been using a ground fault I?m sure this circuit would have worked fine. I just can?t wrap my head around why the GFCI would trip when the ground wire touched the neutral. It was the third receptacle in series after the ground fault.