I have four 170 watt panels that will be installed end to end on the port side of the roof.
I intend to wire in a 2S2P configuration with #10 (possibly #8) wire. Panels 1 and 2 will be in series and a cable run to a combiner box. Panel 3 and 4 likewise.
I'm looking at a cable length of 10' and 23' respectively.
Using the panel specs for voltage and current at max power (17.8v & 9.55a) see a voltage drop of 0.24v (0.67%) on the 10' run and 0.59v (1.66%) on the 23' run.
Is this difference of any real consequence?
Thanks,
Tom