First off, this furnace is on our park model, but still holds true. We noticed it was blowing but no warm air. Bad time of year for that. Anyway, My 2 bro-n-laws and I started in on it with a couple of ideas. First off, none of us had dived into a furnace fix before, here?s our result.
1. Replaced the sail switch, which looked bad but wasn?t sure. No change.
2. Tested igniter to make sure of spark. It was ok.
3. At this point and through next few steps, when it was on, furnace seemed to be pulsing air.
4. Made sure we cleaned out any apparent mud dobber homes. None readily seen, however did finally see some up the exhaust pipe.
5. No change.
6. Removed and replaced burner. Again, it was in bad shape, appearance wise.
7. No change.
8. Removed orifice, blew it out... yes residue could be seen floating in,the air.
7. This time, you could really here when burner lit. IT worked!
All that to say, taking it apart for each step wasn?t bad, but took some patience in where screws are located.
Word of advice, it helps to have a magnetic set sockets and about 3 extensions to reach some.
1. Replaced the sail switch, which looked bad but wasn?t sure. No change.
2. Tested igniter to make sure of spark. It was ok.
3. At this point and through next few steps, when it was on, furnace seemed to be pulsing air.
4. Made sure we cleaned out any apparent mud dobber homes. None readily seen, however did finally see some up the exhaust pipe.
5. No change.
6. Removed and replaced burner. Again, it was in bad shape, appearance wise.
7. No change.
8. Removed orifice, blew it out... yes residue could be seen floating in,the air.
7. This time, you could really here when burner lit. IT worked!
All that to say, taking it apart for each step wasn?t bad, but took some patience in where screws are located.
Word of advice, it helps to have a magnetic set sockets and about 3 extensions to reach some.