Author Topic: RV Solar breaker sizing  (Read 1973 times)

Cholmes100

  • Posts: 3
RV Solar breaker sizing
« on: June 23, 2019, 07:27:02 AM »
Hi everyone, like a lot of you I would like to, and I am in the process of installing solar on my RV, I thought it would be fun and allows for some "boondocking" I have 4 panels 19 v/ 8.9 amps.  I am going to parallel two and two to give me 640 watts, 38 v @ 16.8 amps. Wiring from the panels is whatever came on them and I would like to install a breaker/switch between the panels and charge controller and between the charge controller and batteries.
Charge controller MPPT 30 amps
4 12 V 96 Amp hour batteries

My issue is after hours of searching I cannot get an actual answer, I just get led down the road of 100 more questions. Some say I don't need to install a breaker and will argue the point but I want to be able to isolate the panels from the charge controller and the controller from the batteries for my own reasons. Can anyone here that is really familiar with solar give me the straight up answer to these questions? I would really appreciate it so I can order what I need and get on with it. I have attached an image of the style breaker I thought I would use.

Utclmjmpr

  • ---
  • Posts: 4528
Re: RV Solar breaker sizing
« Reply #1 on: June 23, 2019, 07:54:21 AM »

 Just something else to get corroded and cause problems.>>>Dan
Vary rare American Tradition 38TT/330 turbo Cummins
Last year Jeep liberty 4 down
72 VW Baja 4 down
Cedar City, Utah
USAF vet. 59-63
FMCA F312919
 
You can't fix stupid,, but you can numb it with a 2X4

Gary RV_Wizard

  • Forum Staff
  • ---
  • *
  • Posts: 71220
  • RVer Emeritus
Re: RV Solar breaker sizing
« Reply #2 on: June 23, 2019, 08:28:48 AM »
Quote
Some say I don't need to install a breaker and will argue the point but I want to be able to isolate the panels from the charge controller and the controller from the batteries for my own reasons.

Not sure why you are asking. You say you have your own reasons for it, so other's reasons (or lack there-of) would seem to be irrelevant.  You don't need to install that breaker to make the system work properly, but you can certainly have one to meet whatever your other reasons my be.
If you are doubtful about your own reasons, please state what they are and the rest of us can comment on them, pro or con.
Gary
--------------
Gary Brinck
Summers: Black Mountain, NC
Home: Ocala National Forest, FL

KandT

  • ---
  • Posts: 1394
Re: RV Solar breaker sizing
« Reply #3 on: June 23, 2019, 09:23:26 AM »
Maybe try a solar forum?  I don't see why solar in an RV would be substantially different than in a small farm type application that is not tied to the grid.
2019 Ford F250 6.7 Deisel Crew Cab
2005 Winnebago Vectra 36RD - SOLD
American Car Dolly - SOLD
2009 Accord Toad - SOLD
Figuring out my next purchase.

solarman

  • ---
  • Posts: 381
Re: RV Solar breaker sizing
« Reply #4 on: June 23, 2019, 09:39:09 AM »
Hi everyone, like a lot of you I would like to, and I am in the process of installing solar on my RV, I thought it would be fun and allows for some "boondocking" I have 4 panels 19 v/ 8.9 amps.  I am going to parallel two and two to give me 640 watts, 38 v @ 16.8 amps. Wiring from the panels is whatever came on them and I would like to install a breaker/switch between the panels and charge controller and between the charge controller and batteries.
Charge controller MPPT 30 amps
4 12 V 96 Amp hour batteries

My issue is after hours of searching I cannot get an actual answer, I just get led down the road of 100 more questions. Some say I don't need to install a breaker and will argue the point but I want to be able to isolate the panels from the charge controller and the controller from the batteries for my own reasons. Can anyone here that is really familiar with solar give me the straight up answer to these questions? I would really appreciate it so I can order what I need and get on with it. I have attached an image of the style breaker I thought I would use.

it is good practice to fuse both sides of the charge controller.
I would recommend either BlueSea 285 series or Bussman 25X series breakers.
do yourself a favor and avoid the cheap china breakers found on ebay.

also for 640 Watts of panels you will need a 50 Amp controller ( 640 / 12 = 53 )
using a 30 A with ( 96 * 4 = 384 Ah of capacity ) will not make the C/10 minimum charge rate ( 38.4 A )
unless you are moving to 24 Volts. ?

KZ MXT20 480 W solar
ORV 24RKS 960 Watts solar
48V LFP, 2000W inverter/charger
Ram 2500 CTD

solarman

  • ---
  • Posts: 381
Re: RV Solar breaker sizing
« Reply #5 on: June 23, 2019, 09:44:11 AM »
Maybe try a solar forum?  I don't see why solar in an RV would be substantially different than in a small farm type application that is not tied to the grid.


as an off grid designer, I can tell you there are many differences in requirements and the implementation
of these systems. their use cases are very different.


and moderator, could you please move this thread to the solar section, thanks
« Last Edit: June 23, 2019, 09:54:00 AM by solarman »
KZ MXT20 480 W solar
ORV 24RKS 960 Watts solar
48V LFP, 2000W inverter/charger
Ram 2500 CTD

Cholmes100

  • Posts: 3
Re: RV Solar breaker sizing
« Reply #6 on: June 23, 2019, 10:05:04 AM »
Why I am asking is obvious, not sure what my reasons are factor into the question, but my "reasons" are so I can shut off the panels before and after the charge controller instead of crawling up on the roof and covering them. Again, not sure why I want to do it matters. I also know I don't have to install a breaker to make it work properly but installing one won't make it not work properly. Moderator, I couldn't find a solar section or I missed it so that is why I posted here, sorry for that.

Larry N.

  • ---
  • Posts: 7014
  • Westminster, CO
Re: RV Solar breaker sizing
« Reply #7 on: June 23, 2019, 10:12:02 AM »
Quote
I couldn't find a solar section or I missed it
It's a "child" of the TECH forum.
Larry and Mary Ann N.
2016 Newmar Ventana 3709 -ISB6.7 XT 360HP
2015 Wrangler Sahara Unlimited toad
Formerly: Trailmanor 2720SL, Bounder, Beaver
  de N8GGG

Kevin Means

  • ---
  • Posts: 4917
  • SolaRVector
    • SolaRVector
Re: RV Solar breaker sizing
« Reply #8 on: June 23, 2019, 11:05:34 AM »
"Best practice" would be to install circuit protection between the panels and the controller, and the controller and the batteries, but I think you'll find that very few RVers have fuses or breakers between the panels and controller - and few (if any) have experienced any problems. I would strongly recommend, however, installing a catastrophic fuse or breaker between the controller and batteries - as close to the batteries as possible.

FWIW, I installed DC disconnect switches between my panels and the controller, and the controller and batteries, and the switches are co-located next to the controller. They allow me to remove power to both sides of the controller for any number of reasons. I suppose that if you were dead-set on having breakers, you could install circuit breaker switches instead of simple switches.

The wires attached to panels are usually only short leads, so in all likelihood you will be running additional wire. You didn't mention what kind of RV you have, and long wire runs, or thin gauge wire can cause unnecessary voltage loss. Just food for thought.

Kev
2011 Winnebago Tour 42QD
Towing a Jeep Rubicon Unlimited LJ
RVI Brake 2, TST 507 TPMS, 960 watts of solar, SolaRVector tilt
Lakeside, California

HueyPilotVN

  • ---
  • Posts: 2144
Re: RV Solar breaker sizing
« Reply #9 on: June 23, 2019, 12:30:48 PM »
Easy solution that I did was to place fuses before and after the controller.  easy to unscrew and remove the fuse to isolate the controller.

Bill Waugh
2 Jeep Commanders
Mustang Bracket Race Car
Retired from the road to Lake Havasu after 35 years on the road
Now just another Lurker

Cholmes100

  • Posts: 3
Re: RV Solar breaker sizing
« Reply #10 on: June 23, 2019, 01:01:17 PM »
Yes, breaker switches. Question remains: What amperage's?

HueyPilotVN

  • ---
  • Posts: 2144
Re: RV Solar breaker sizing
« Reply #11 on: June 23, 2019, 01:39:36 PM »
I would look at the max operating current for the controller and then add a little to prevent blowing the fuse with normal operation.  There is no single answer because the current of the specific controller will determine what to use,
Bill Waugh
2 Jeep Commanders
Mustang Bracket Race Car
Retired from the road to Lake Havasu after 35 years on the road
Now just another Lurker

zulu

  • ---
  • Posts: 180
Re: RV Solar breaker sizing
« Reply #12 on: June 23, 2019, 02:06:01 PM »
Yes, breaker switches. Question remains: What amperage's?

Remember, fuses protect the wires. So if your wiring is rated at 15A, use a 15A fuse or less.

I have a similar setup -- three, 245W panels in parallel.
https://rvseniormoments.com/projects/solar-panels/

I suggest you check out the MidNite Solar Forums:
http://midniteftp.com/forum/

Also, besides charge controllers, MidNite Solar sells breakers, breaker boxes, and combiners.
http://www.midnitesolar.com/products.php?menuItem=products&productCat_ID=16&productCatName=Breakers

http://www.midnitesolar.com/products.php?menuItem=products&productCat_ID=10&productCatName=Small%20Breaker%20Boxes

Full Timer

KandT

  • ---
  • Posts: 1394
Re: RV Solar breaker sizing
« Reply #13 on: June 23, 2019, 07:58:34 PM »

as an off grid designer, I can tell you there are many differences in requirements and the implementation
of these systems. their use cases are very different.


and moderator, could you please move this thread to the solar section, thanks

Sorry solarman. 
2019 Ford F250 6.7 Deisel Crew Cab
2005 Winnebago Vectra 36RD - SOLD
American Car Dolly - SOLD
2009 Accord Toad - SOLD
Figuring out my next purchase.

Lou Schneider

  • Global Moderator
  • ---
  • *
  • Posts: 10336
Re: RV Solar breaker sizing
« Reply #14 on: June 24, 2019, 02:15:37 AM »
Solar panels have a maximum current into a short circuit that's only slightly above their operating current.  For example, a Renogy 100 watt solar panel produces 5.3 amps at it's Maximum Power Point and only 5.75 amps into a short circuit.  This makes a solar array inherently safe as long as it's wiring is properly sized.

Nothing catastrophic happens if you short the output of a solar panel, it just produces it's rated short circuit current.  There's no need for a circuit breaker since a circuit fault won't produce enough current to trip it.

Batteries on the other hand are capable of discharging thousands of amps into a short.  They absolutely need a catastrophic fuse that is large enough to pass all of the current the wiring can normally handle but will blow before the wires have a chance to heat up to a dangerous level if there's a short.

Since solar panels are inherently safe, you can use anything you want to disconnect them for service.  Pull apart an Anderson Powerpole connector set or flip a battery disconnect switch.  Or just remove the wire from the input of the controller.  You're not limited to using a circuit breaker.
« Last Edit: June 24, 2019, 02:51:28 AM by Lou Schneider »

solarman

  • ---
  • Posts: 381
Re: RV Solar breaker sizing
« Reply #15 on: June 24, 2019, 10:25:01 AM »
Sorry solarman.

no need to apologise,  :) :)
KZ MXT20 480 W solar
ORV 24RKS 960 Watts solar
48V LFP, 2000W inverter/charger
Ram 2500 CTD

solarman

  • ---
  • Posts: 381
Re: RV Solar breaker sizing
« Reply #16 on: June 24, 2019, 10:37:02 AM »

Nothing catastrophic happens if you short the output of a solar panel, it just produces it's rated short circuit current.  There's no need for a circuit breaker since a circuit fault won't produce enough current to trip it.

Since solar panels are inherently safe

You're not limited to using a circuit breaker.


sadly incorrect, this may be the case for a single panel, but it's a different story when multiple series/parallel strings are
combined, then we have a situation where failures in one string can cause damaging currents
to destroy the other strings, hence the requirement to provide combiner boxes and fuses.

secondly, solar panels are not intrinsically safe, there is a case for reverse polarity bypass diodes to short and cause
sufficient  overheating to cause ignition. this does occur, although not frequently ( i have seen panel interface boxes melted and burnt on large installations )
and is probably of minimal concern for a low wattage RV installation.

although not strictly necessary, there is a valid case for a circuit breaker in the solar string, one particular function is to act as a switch
for disconnecting the array from the controller. some MPPT controllers have issues with an active array connected when the batteries are disconnected.