AJW said:
I have been using 6 Lifeline 6V AGMs for 5 years in my coach. This year arrived at Yuma (Imperial Dam) and it seems they have gone to hell in a hand basket! After a full charge (solar) to 100% via TM2025 about 4:00 am I get a low voltage alarm on my fridge. Down to 11.0 V. The other night watching a hockey game my inverter shut down on low voltage again after having charged them fully. I have noticed in the last 6 months they have not been lasting nearly as well as they used to. I phoned a dealer and he stated that the Lifelines are not what they used to be! Methinks I am going to replace them with the Full River GC224 6 V AGMs. Any thoughts?
part of the problem is the parallel setup.. I assume you have a 2S3P pack..
if you are going to parallel then any agm will do, you do not need premium batteries as you are unable to take full advantage of them.
have you ever run an equalizing cycle on these batteries ?
lifeline/concorde are one of a few that allow this. i'll wager you have not and are now sitting on sulfated batteries and wonder why they no longer perform.
replacement cost .... most 6 V GC2 like crown/trojan/fullriver are about $300 each
so you will spend $1800 or so for another 5 years.
if you insist on parallel arrangements, then why not consider
12 V 100 A/hr drop in lithium such as the battelborn. you will need approx 400 Ahr
to replace the 600 Ahr of agm.. so now thats close to $3600 for a possible 10 year battery and no parallel issues
that lead acid will give you. cost is approx that of agm if amortized over 10 years..
you will need to set your bulk/absorb to 14.4 V and float to 13.6 V