We have a 2019 Pinecrest 305 RLP 5th wheel by Vanleigh with 2 Coleman Mach AC units running on 50 amps. Most of the time both units operate fine. Sometimes the units will run for less than a minute then shutdown. Most technicians state that is a problem with the pedestal at the site and not anything wrong with the trailer or AC units. Both units--running together or separately--exhibit the same behavior. When they do shut down, one of the GFCI outlets also gets tripped.
No breakers are tripped -- in the trailer or at the pedestal -- but one GFCI does trip at the same time. This would seem to suggest that there is some power issue that causes the GFCI and AC units to trip. Turning off the breaker for the circuit that has the GFCI does not stop the AC units from shutting down. When turning off ALL breakers except for one 20-amp breaker for one of the AC units, that AC unit still shuts down.
Running the AC fan only does not cause it to shut down.
Even though there is at least 120 volts on each leg, the current under load may be inadequate to run the AC compressor(s).
Has anyone seen similar behavior?
Again, many parks and my home pedestal does not cause this problem. So, it would seem that there is nothing wrong with the units or trailer wiring. Any work arounds?
Is there someway to test the pedestal (since it needs to be under load for current and not just the voltage potential difference)?
Any other suggestions?
No breakers are tripped -- in the trailer or at the pedestal -- but one GFCI does trip at the same time. This would seem to suggest that there is some power issue that causes the GFCI and AC units to trip. Turning off the breaker for the circuit that has the GFCI does not stop the AC units from shutting down. When turning off ALL breakers except for one 20-amp breaker for one of the AC units, that AC unit still shuts down.
Running the AC fan only does not cause it to shut down.
Even though there is at least 120 volts on each leg, the current under load may be inadequate to run the AC compressor(s).
Has anyone seen similar behavior?
Again, many parks and my home pedestal does not cause this problem. So, it would seem that there is nothing wrong with the units or trailer wiring. Any work arounds?
Is there someway to test the pedestal (since it needs to be under load for current and not just the voltage potential difference)?
Any other suggestions?