The results are in. After a long wait because of the virus. I have the answer to my problem. To recap I had replaced a two ducked AC/HP system with a new CC2 thermostat. The install went easy as it is a plug and play system for the most part. The problem I was having was that I did not have a med fan speed. This played havoc with the auto setting. The CC2 in auto runs low to a 4 degree difference and med to a 8 degree difference and over that it is on high. The new system is so much quieter than the old system and part of that is the fan speed selection. I had a certified dometic tech look at it 3 different times and his answer was that I had a two speed heatpump. After much research I found that the factory does not hook up the med fan wire ( yellow) for a change out as they do not know if you have a thermostat that will support it. To fix the unit is fairly simple. Remove cowl and foam cover of AC/HP upper unit. You will see a yellow wire that is caped off. Run this wire down to the controller and remove the cover and attach a wire connector to the yellow wire and plug it into the board on the med fan. It will be labeled. It might have a orange wire already connected to it but that is from the heatstrip plug that is not being used in my case. If it was I would tie the two together. Reinstall all covers and enjoy three fan speeds on your new AC/HP units in auto mode. The wife will love you.