Author Topic: RVP 8000 Roof AC Unit not working  (Read 4033 times)

02 windsport

  • ---
  • Posts: 25
RVP 8000 Roof AC Unit not working
« on: August 09, 2009, 07:11:09 PM »
   My rear roof air has stopped functioning. The fan runs, however when I place the thermostat to cool the compressor draws enough current to trip the 20 amp breaker at the generator. I pulled info from the net for diagnosis and have done some testing. I bypassed the start relay (purple and black wires) and it continues to trip the breaker at the generator. I guess I need to climb on top and check at the compressor next. Any suggestions?????

007

  • ---
  • Posts: 69
Re: RVP 8000 Roof AC Unit not working
« Reply #1 on: August 13, 2009, 06:33:08 PM »
How about a starting capacitor check the PPL website they have them.
Newmar KS-3740 W-22 03------- 99 MA ---98 KS
96 Bounder 34J FORD V-10 - 88 GB FORD-460

Gary RV_Wizard

  • Forum Staff
  • ---
  • *
  • Posts: 61015
  • RVer Emeritus
Re: RVP 8000 Roof AC Unit not working
« Reply #2 on: August 13, 2009, 07:13:00 PM »
Yeap - your "hard start" capacitor has probably failed. It's easy enough to replace yourself if you have basic skills. Get the new one, turn the breaker for the a/c off, pull the shroud off  (up on the roof) and look for a part on the circuit board that looks like the new one. Should not need any soldering - they normally just clip into place.

Here is an article on this repair:

http://www.modmyrv.com/2009/05/27/rv-air-conditioner-hard-start-capacitor
Gary
--------------
Gary Brinck
Summers: Black Mountain, NC
Home: Ocala National Forest, FL

02 windsport

  • ---
  • Posts: 25
Re: RVP 8000 Roof AC Unit not working
« Reply #3 on: August 13, 2009, 08:11:04 PM »
Tested all 3 caps and found that the start cap wouldn't store voltage. Ordered the hard start kit today from the local RV dealer. Should be here on Tuesday. I'll keep you posted.

02 windsport

  • ---
  • Posts: 25
Re: RVP 8000 Roof AC Unit not working
« Reply #4 on: August 22, 2009, 04:47:43 PM »
  Wound up being the run capacitor. All OK and Cool Now !

Gary RV_Wizard

  • Forum Staff
  • ---
  • *
  • Posts: 61015
  • RVer Emeritus
Re: RVP 8000 Roof AC Unit not working
« Reply #5 on: August 22, 2009, 09:27:53 PM »
Glad to hear everything is cool again, Windsport. Now go have some fun!
Gary
--------------