RVP 8000 Roof AC Unit not working

The friendliest place on the web for anyone with an RV or an interest in RVing!
If you have answers, please help by responding to the unanswered posts.

02 windsport

Active member
Joined
Mar 15, 2009
Posts
25
Location
Lancaster, NY
  My rear roof air has stopped functioning. The fan runs, however when I place the thermostat to cool the compressor draws enough current to trip the 20 amp breaker at the generator. I pulled info from the net for diagnosis and have done some testing. I bypassed the start relay (purple and black wires) and it continues to trip the breaker at the generator. I guess I need to climb on top and check at the compressor next. Any suggestions?????
 
Yeap - your "hard start" capacitor has probably failed. It's easy enough to replace yourself if you have basic skills. Get the new one, turn the breaker for the a/c off, pull the shroud off  (up on the roof) and look for a part on the circuit board that looks like the new one. Should not need any soldering - they normally just clip into place.

Here is an article on this repair:

http://www.modmyrv.com/2009/05/27/rv-air-conditioner-hard-start-capacitor
 
Tested all 3 caps and found that the start cap wouldn't store voltage. Ordered the hard start kit today from the local RV dealer. Should be here on Tuesday. I'll keep you posted.
 