I have a 2000 Winnebago 27P Class C and I am hoping someone can help because I am at my wits end trying to figure out the gremlins that are plaguing my rooftop Coleman air conditioner. It will be a while before I can take the rig to ANY shop, but I can follow diagrams and directions, and I am hoping someone can help me get this solved.
After very carefully following the RVP troubleshooting guide, I recently replaced the control box in the ceiling and the thermostat and had the fan motor rebuilt.
It turned out the compressor relay in the new j-box was bad, so I went and got yet another one. (When I bypassed the relay, the compressor kicked on.)
Now with this THIRD j-box, I am NOT getting 115 volts on the 1 & 3 pins to the compressor. AND I am only getting 6 volts to the red & blue (DC-) and red & yellow (fan) wires on the thermostat. RVP says it should be 12 volts. And...those wires were getting 12 volts when the old thermostat was in place, so what the heck could have happened that now I am only getting 6 volts?
Beyond that RVP says only "restore 12 volts to the thermostat". Well ok. But how the heck do I do that? I was going to try to trace the wires down the wall from the thermostat, but they are really anchored in there somehow. They definitely go DOWN the wall, so I was hoping they would emerge at floor level somewhere, and lead me to the 12 volt power source, but I can't find them anywhere.
And... where the heck is my inverter/converter or whatever it is? I thought it should be under the refrigerator near the power panel with the circuit breakers, but I have no clue if it is or not. I have attached a picture of what I found there. What is it? (Besides dirty? - - and I am afraid to reach in there to clean it! It is also very hot to the touch!)
EDIT:
I guess that IS the converter. It is putting 12.5 volts to appropriate places, like to the fuse panel next to the circuit breakers. But where did the other 6 volts wander off to on their way to the thermostat?
After very carefully following the RVP troubleshooting guide, I recently replaced the control box in the ceiling and the thermostat and had the fan motor rebuilt.
It turned out the compressor relay in the new j-box was bad, so I went and got yet another one. (When I bypassed the relay, the compressor kicked on.)
Now with this THIRD j-box, I am NOT getting 115 volts on the 1 & 3 pins to the compressor. AND I am only getting 6 volts to the red & blue (DC-) and red & yellow (fan) wires on the thermostat. RVP says it should be 12 volts. And...those wires were getting 12 volts when the old thermostat was in place, so what the heck could have happened that now I am only getting 6 volts?
Beyond that RVP says only "restore 12 volts to the thermostat". Well ok. But how the heck do I do that? I was going to try to trace the wires down the wall from the thermostat, but they are really anchored in there somehow. They definitely go DOWN the wall, so I was hoping they would emerge at floor level somewhere, and lead me to the 12 volt power source, but I can't find them anywhere.
And... where the heck is my inverter/converter or whatever it is? I thought it should be under the refrigerator near the power panel with the circuit breakers, but I have no clue if it is or not. I have attached a picture of what I found there. What is it? (Besides dirty? - - and I am afraid to reach in there to clean it! It is also very hot to the touch!)
EDIT:
I guess that IS the converter. It is putting 12.5 volts to appropriate places, like to the fuse panel next to the circuit breakers. But where did the other 6 volts wander off to on their way to the thermostat?