Ok so I will try to explain this clearly, I have done a lot of trouble shooting based on posts I have read here and other sources (manual) if you have any ideas on what it could be please chime in. I could be doing something wrong and just not realize it, This RV is new to me.
2015 Itasca Sunstar 35F 8900mi just picked it up last week. Its beautiful
I will try to cover this in steps as to what I have done so far.
When I plug into 30amp everything works fine in the coach. My "Energy Management system" inside the coach is lit up with all the monitored components (loads) lit up and says 30a
here's the issue when (unplugged from 30amp)
When I start the Generator I hear the clunk of the switch,
On the "Energy management system" inside the coach all the load lights lite up momentarily and they all go off in quick succession like its shedding the loads one right after the other.
My Outlets all work, my Microwave works.. but AC/ does not. Every few minutes all the lights light up again and then go out. If the AC is set to run it kicks on for a few seconds but shuts off as the "load is shed"
Using a voltmeter I measured the transfer switch voltages in the switch box both before and after I started the generator and the voltage is appropriate per the manual. There is a green led on circuit board on the generator side of the transfer switch that is illuminated when the generator is on
I checked the two breaker switches on the front of the onan generator and they are both on I cycled them (with the generator off)
I cycled all the breakers in the box near the door , I took off the panel on the breaker box and I know there is a piece of the energy management system in there, it looked fine all screws tight.
So what did I miss, do you have suggestions for me?
Thank you
Greg in Rhode ISland
2015 Itasca/Winn Sunstar 35F
2015 Itasca Sunstar 35F 8900mi just picked it up last week. Its beautiful
I will try to cover this in steps as to what I have done so far.
When I plug into 30amp everything works fine in the coach. My "Energy Management system" inside the coach is lit up with all the monitored components (loads) lit up and says 30a
here's the issue when (unplugged from 30amp)
When I start the Generator I hear the clunk of the switch,
On the "Energy management system" inside the coach all the load lights lite up momentarily and they all go off in quick succession like its shedding the loads one right after the other.
My Outlets all work, my Microwave works.. but AC/ does not. Every few minutes all the lights light up again and then go out. If the AC is set to run it kicks on for a few seconds but shuts off as the "load is shed"
Using a voltmeter I measured the transfer switch voltages in the switch box both before and after I started the generator and the voltage is appropriate per the manual. There is a green led on circuit board on the generator side of the transfer switch that is illuminated when the generator is on
I checked the two breaker switches on the front of the onan generator and they are both on I cycled them (with the generator off)
I cycled all the breakers in the box near the door , I took off the panel on the breaker box and I know there is a piece of the energy management system in there, it looked fine all screws tight.
So what did I miss, do you have suggestions for me?
Thank you
Greg in Rhode ISland
2015 Itasca/Winn Sunstar 35F