Can anyone help out? I am on the road now... It runs but no power. Reseached a long time.
I remember that it suddenly went out of power when powering the facilities.
The following tests are done.
1. Circuit breaker was reset. no help.
2. Tested the output directly from the generator's female socket, which says 87volts AC. See attched picture
3. Uses another generator, all facilities run fine.
4. The faulty code says service required, which I am planning to do after my trip. But does this lead to power failure?