If they are rated for 30 amps then it would not be safe to pull 50 amps out of each one. The rating is THE RATING. Besides each trailer with a 30 amp service should have a 30 amp master or main breaker inside the converter panel.
Except that in the case presented, one of the RV's is wired for 50 amp service, so there is no 30 amp breaker anywhere between the source and load.If they are rated for 30 amps then it would not be safe to pull 50 amps out of each one. The rating is THE RATING. Besides each trailer with a 30 amp service should have a 30 amp master or main breaker inside the converter panel.
If the wire and contacts are capable of handling 50 amps, then of course they can handle it. Is it possible the wiring and 30 amp outlets are of capable handling a continuous 50 amps? Not likely. There is usually some safety over rating built in to electrical devices, but just how much over rating is an unknown.My question is really about the 30-amp RV outlets themselves. Can they safely handle 50 amps (if the wire to them can). And if so, can it be a continuous 48 amps?
I assume it's probably not much of an issue as long as there is no juice when plugged in and removed as long as it's a good connection when used.
I just am not sure what the rating means--or even if the rating on a plug/outlet is really the max current it can handle, even if off when plugged in or out.
-Don- Reno, NV
That's a good point. If it is used as intended, you're not going over the 30-amps anyway.Besides each trailer with a 30 amp service should have a 30 amp master or main breaker inside the converter panel.
I assume there are many variables besides the current. Such as if there is a load when plugged in and unplugged, weather, dampness, how clean the contacts are, etc. & all of it is taken into consideration with the rating.Not likely. There is usually some safety over rating built in to electrical devices, but just how much over rating is an unknown.
Are you planning on using TWO adapters in series to do such?One is 30 amp and the other is a 50 amp setup
Yes, the 30 amp RV will plug into the 'Y' adapter directly and the 50 RV will plug in via a 30/50 adapter.Are you planning on using TWO adapters in series to do such?
-Don- Reno, NV
Which brings back the safety issue I mentioned. But as long as not going over 30 amps total on the 50-amp RV, no issue.Yes, the 30 amp RV will plug into the 'Y' adapter directly and the 50 RV will plug in via a 30/50 adapter.
Simple answer is yes.
In this case you probably have one of these adapters?
View attachment 157925
You may have each 30A plug on a separate 50A leg but I would have to check it with a meter to be sure. If you measure between the hot pins of each 30A plug it will show 240V if on separate legs or 0V if they share the same leg. Either way, if all you want is to keep the batteries up and possibly use a few lights it should work as a shared leg would still allow about 15a each. If it is on separate 50a legs the RV limit for the 30A RV will be it's own main power circuit breaker.
Each 30 amp leg of the adapter is fed from a separate 50 amp leg from the source. A single 50 amp 6,000 watt leg will support two A/C units without tripping the breaker.Electrically if you plug the green splitter into a 50amp outlet and one 30amp female into a 30amp RV, that's fine. 30 amp protection at the RV and 50amps on the leg.
If you plug a 30 to 50amp dogbone into the 50amp RV you will get 120V on each leg sharing a 50amp feed. There is nothing to control the balance of load so in theory you could draw 50 amps through one leg of the 30/50 dogbone.
For running the power converters on 2 RVs this should be fine. I expect the 50 amp park panel will blow if the 50amp RV turns on more than one A/C.
View attachment 157933
View attachment 157934
If you use that device to split a 50A outlet that has the typical 2 ganged cricuit breakers supplying it and then you use a 50/30a adapter at each 30A plug to connect a 50a RV to each of the plugs, the wire and connections of the splitter become the limiting factor since there is now on 30A protection for wire sized for only 30a. You might get away with doing this with only 1 drawing more than 30a at least for a time but if both sides push the 50a limit the splitter will most likely get hot enough to melt it.So you're saying it's okay to draw 50 amps out of a 30-amp adapter outlet without any CB tripping?
No common circuit breaker is designed to operate at the upper current limit continously. The actual design of circuit breakers is that they have a long-time limit that is usually about 80% of the stated limit, a short-time limit that is typically 120% of the stated limit and an instantanious trip point that is typically 150% or more of the stated limit. The higher one allows for surge currents of a starting motor and similar things.My question is really about the 30-amp RV outlets themselves. Can they safely handle 50 amps (if the wire to them can). And if so, can it be a continuous 48 amps?
That's what I said.Each 30 amp leg of the adapter is fed from a separate 50 amp leg from the source. A single 50 amp 6,000 watt leg will support two A/C units without tripping the breaker.
My question is really about the 30-amp RV outlets themselves. Can they safely handle 50 amps (if the wire to them can). And if so, can it be a continuous 48 amps?