Adapting a 14-30 Dryer Outlet for a 30 Amp RV

Thread Summary

Summarized on:
Original Member Title: Plug confusion.
This AI-generated summary may contain inaccuracies. Please refer to the full thread for complete details.
A member asked whether a newly installed garage outlet labeled 30A/125/250V could be adapted for a 30 amp RV plug. Members identified it as a 120/240V dryer-style outlet and agreed the RV should not be plugged into it directly, since a 30 amp RV TT-30 connection requires 120V with one hot, one neutral, and one ground.

Several members said a properly wired 14-30 to TT-30 adapter can supply 30A/120V by using one hot leg plus neutral and ground, while others urged having a qualified...
More...
Not unsafe but there is already 30 amps of 120V there which is the max that the RV can use. The dogbone is $50. He could probably even get the electrician to come back and install the correct outlet if it was in error, but that's where one has to make sure the TT-30 gets wired correctly, especially by a rookie electrician which appears to be the case.

Also, you'd need the 5,000 watt one to get the full 3,600 watts for the RV, but even that wouldn't work since the 120 volt sockets are only 20 amps.
 
Last edited:
I don't see a way to get 30 amps at 120V out of it.
You must have meant 60-amps total in above, 30-amps to two RVs.

Didn't you say it was a 120-N-120 VAC outlet? That means 120 VAC at 30 amps each for a total of 7,200 watts.

Across the two hots will be 240 VAC @ 30 amps, still 7,200 watts (no power gained, no power lost).

Now the transformer, step down the voltage to half (120 VAC) as it increases the current capacity to double 60-amps).

120 VAC times 60 amps=7,200 watts.

Perhaps a 5% loss at the transformer, still very close to 60 amps at 120 VAC (the 7,200 watts).

And then no reason to be concerned with the neutral.


-Don- Reno, NV
 
You must have meant 60-amps total in above, 30-amps to two RVs.

Didn't you say it was a 120-N-120 VAC outlet? That means 120 VAC at 30 amps each for a total of 7,200 watts.

Across the two hots will be 240 VAC @ 30 amps, still 7,200 watts (no power gained, no power lost).

Now the transformer, step down the voltage to half (120 VAC) as it increases the current capacity to double 60-amps).

120 VAC times 60 amps=7,200 watts.

Perhaps a 5% loss at the transformer, still very close to 60 amps at 120 VAC (the 7,200 watts).

And then no reason to be concerned with the neutral.


-Don- Reno, NV
The bottom line is that no transformer is needed to power the OP's 30 amp RV. Only the listed adapter or a knowledgeable electrician to swap out the outlet.
 
You must have meant 60-amps total in above, 30-amps to two RVs.

Didn't you say it was a 120-N-120 VAC outlet? That means 120 VAC at 30 amps each for a total of 7,200 watts.

Across the two hots will be 240 VAC @ 30 amps, still 7,200 watts (no power gained, no power lost).

Now the transformer, step down the voltage to half (120 VAC) as it increases the current capacity to double 60-amps).

120 VAC times 60 amps=7,200 watts.

Perhaps a 5% loss at the transformer, still very close to 60 amps at 120 VAC (the 7,200 watts).

And then no reason to be concerned with the neutral.


-Don- Reno, NV
No, what I meant is there is no 30 amp 120 volt outlet on the transformer, just 3-120 volt 20 amp outlets.
 
On the subject of 2 30 amp RVs, just for fun, that existing 10/3 would still work. One line to each TT-30, pigtail the neutral into two and pigtail the ground into two then you have a multiwire branch circuit (MWBC) with 2 outlets capable of 3,600 watts each at 120 volts.

As long as you use a 2 pole 30 amp breaker installed so that there is 240V between the two lines everything is safe and legal.
 
No, what I meant is there is no 30 amp 120 volt outlet on the transformer, just 3-120 volt 20 amp outlets.
OIC, but all three are just in parallel.

On the subject of 2 30 amp RVs, just for fun, that existing 10/3 would still work.
Yep, as I said, the only problem is getting the correct adapters. Can easily be made as a plug-in using all three (only safe with all three 120 VACs plugged in!). IOW, three 20-amp outlets to two RV-30's.

Better yet is to see if there is a 240/120 vac transformer available that has two RV-30's as its output. If not, can make the adapters.

I have made various weird AC adapters for my electric motorcycles, such as shown here, where it says "I modified a Marinco 6375M AC plug and made an adapter." BTW, do you know what that outlet is called ( 240 VAC outlet for some type of boat?):

First I have seen:

1780408988895.png
 
The bottom line is that no transformer is needed to power the OP's 30 amp RV. Only the listed adapter or a knowledgeable electrician to swap out the outlet.
Or we can say:

"The bottom line is that no electrician is needed to power the OP's 30 amp RV"

Will cost less and will have more choices of what the outlet can do.

-Don- Reno, NV
 
I had to look it up. That configuration has an interesting history. It is a "California Standard" 125/250 volt twist lock used for emergency power, construction power and marine power.
From that, I was able to look it up the number. It's a CS6364.

Perhaps the "CS" stands for "California Standard."

It costs $116.28 on Amazon:

1780413130669.png

 
Or we can say:

"The bottom line is that no electrician is needed to power the OP's 30 amp RV"

Will cost less and will have more choices of what the outlet can do.

-Don- Reno, NV
The posted adapter costs the least and gets the job done. A transformer would be a costly and unnecessary additional failure point. The adapter has one 30 amp socket, and that's all that's needed.
 

Try RV LIFE Pro Free for 7 Days

  • New Ad-Free experience on this RV LIFE Community.
  • Plan the best RV Safe travel with RV LIFE Trip Wizard.
  • Navigate with our RV Safe GPS mobile app.
  • and much more...
Try RV LIFE Pro Today
Back
Top Bottom