I am experiencing similar problems with my Atwood 8535-IV-DCLP as MichaelD123 had stated in his post of Feb. 1, 2016: furnace fires up - but only runs for about 2 seconds, shuts the gas valve, flame goes out, then it re-ignites, burns 2 seconds, goes out, and repeats this cycle without stopping the fan. It will cycle 3-4 cycles then the blower will stop, then within 10 seconds the whole process will start over. I have tested everything I can test: replaced anything that might be a possible problem (?). The last thing I tried was to pull the gas valve/ignition “module” (for lack of a better term) from the unit: attached extension wires to facilitate moving the “module” a few inches from the furnace: connected 12v to the furnace, flipped the reset switch, and the burner fired up and burned perfectly! I ran it for 30 seconds or so before I shut it down, and it seemed to burn flawlessly. Put the “module” back in the furnace, powered it up, and it started the 2 second cycle again.
All this is being done “on the bench”, not in the RV.
Please, any suggestions would be greatly appreciated.