Mark_K5LXP
Senior Member
If the spark path is shorted to ground, the non contact indicator probably won't indicate even with a good coil.
Mark B.
Albuquerque, NM
Mark B.
Albuquerque, NM
Leave the high voltage lead connected to the the circuit board as normal and connect the other end to the contact on the end of the sparkplug. Then put that spark plug where is it making contact with the furnace frame, if you have it grounded. You should be able to see and hear the spark when it fires.When using the spark plug method I connec
Showing my ignorance here but how do I ground the furnace when it's on the bench? As I said previously this is a learning experience for me, and I am learning a lot. thanksLeave the high voltage lead connected to the the circuit board as normal and connect the other end to the contact on the end of the sparkplug. Then put that spark plug where is it making contact with the furnace frame, if you have it grounded. You should be able to see and hear the spark when it fires.
Run a wire from the frame of the furnace to the negative battery post and that will serve well. Your RV as well as motorized vehicles just connect the negative post of the battery to the frame or the chassis and so supply a return for the 12V system that way. On the workbench you need to supply the return to the negative battery post.how do I ground the furnace when it's on the bench?
By "circuit" I merely meant the entire thing, i.e. the igniter itself, the wire to the control board, the connector where it mates to the board, and the ground path at the igniter end. All 4 of those things have to function perfectly to get a spark. Continuity tells you the wire isn't broken but nothing about the other three. The ground path for the igniter is the spark jumping from the igniter tip to nearby metal.I'm not clear on what a faulty igniter circuit refers to other than the igniter wire, its continuity tested good ,
That sounds like you are not getting the return signal from the ignition probe that tells the circuit board that the flame is burning. Have you replaced the ignition probe? That is the most common failure of them in my experience.it initially ignited but went out after a couple of seconds, it went through the sequence of opening the gas valve to light 2 more times with the same results, ignition and then lost flame after a few seconds.
Not sure what you mean by the ignitor. Do you mean the ignitor coil on the board? I put a new board on and it ignited the fuel like same as the old one for a few seconds before going out, that tells me the spark is reaching the electrode tip(I think), any reason I should test the electrode further? I thought the ignitor gap of 1/8" was the distance to the burner head, not the distance between the electrode tips, regardless the tips are 1/8 apart(pic with 1/8 hex).Have you installed a new ignitor ? I think you mentioned that you tested the existing ignitor? How did you test the ignitor ?
Ignitor gap will be in the service manual. Usually around 1/8 inch but look at the specification in the manual.
Is the probe part of the electrode? I don't see what it is if not an electrode part. I just looked at the 7900IIThat sounds like you are not getting the return signal from the ignition probe that tells the circuit board that the flame is burning. Have you replaced the ignition probe? That is the most common failure of them in my experience.
It is the electrode. Between sparks the heat for the burning propane creates a signal back to the circuit board that is too small for most meters to detect but it is there, if working properly.Is the probe part of the electrode?