No, my concern is that if the tap to the 20 amp circuit breaker is only #12 it is not rated for use on a 50 amp circuit and line conductors or grounding conductor could be damaged during a bolted fault. #10 like what the original wiring uses is allowed to be used as the EGC on a 50 amp circuit. (NEC 250.122) I am not concerned with any 30 or 50 amp wiring because all of that has a #10 EGC.Is this what your concern is? The second AC has a 20 A CB so that section is protected. So the concern is that the wiring to that 20A CB shorts, the section to the 50A service could melt?
The original wiring 30A cable to the OEM can be argued has the same situation. But the OEM setup is fed with 50A when folks used adapters.