I am installing a new furnace, I have hooked up the power supply and tried bypassing the thermostat and only get a clicking sound from the furnace nothing else.
ferfer said:The furnace troubleshooting article is missing??? I can see only the title.
If there is air in the propane line, the propane furnace will try to light and shut down. Thus the reason we purge the propane via a stove burner for first use.
Also if the propane is turned on too fast it can cause propane flow problems and thus interfere with furnace operations. Someone correct me or add info., but I think turning of the propane and allow 5 minutes to pass before turning it back on.
Jennifer
Maybe it's a NT-40 furnace. One of the steps in the furnace's control board sequence to start the furnace is checking that the sail switch is open before allowing the blower to come on. The sail switch is located inside the furnace box and is activated by air flow. If it is stuck in the wrong position, maybe due to a hard drop during shipping, it could cause the control board to fault and not allow the blower motor to run in the purge cycle. I'd check to see that the sail switch moves freely. Just remove a few screws to gain access to the inside of the furnace to inspect the switch. The "sail" part of the switch is a small rectangular piece of metal attached to a short metal rod. When the air from the blower motor hits the sail, the switch is activated (closed). The click you hear is the furnace power relay being activated, which is the on/off power to the control board when the thermostat calls for heat.RPIntegrity said:It is a Suburban 40k furnace. Purging the lines would have nothing to do with me just trying to get the blower to run.