Totally non-RV related other than the fact I am building this property to install an RV pad - LOL...
So the well is in my property and the paperwork says it's a 230V 1 hp submersible pump. The power run is about 170-180 feet from the distribution box. I also know they ran 84 feet of 12-3 wire down the casing to power the pump cuz they charged me for it.
So I convert 1 hp @240V to amps and get 4 amps.
Then I check wire sizing for a 170 foot run and the wire sizer tells me I can use 16g copper?
Q1 - Does that sound like I did the calcs right?
Q2 - In overkill mode I am planning to run 12-3 copper in a conduit on a 15amp breaker - Does that sound reasonable?
Thanks is advance.