No AC from 10K Onan generator?

The friendliest place on the web for anyone with an RV or an interest in RVing!
If you have answers, please help by responding to the unanswered posts.

WhiteEagle

Well-known member
Joined
Sep 4, 2009
Posts
349
Location
Wisconsin
at Quartzsite and apparently just 20 min ago lost Ac power from generator..
Alls been fine .. but decided to run generator for an hour or so before bedtime... and them decided to add some load to it for this period..
wife was running microwave, normal coach lights on, 2 computers.. and I turned on two 1500 Watt electric heaters.... seemed like that should have been approx 50-60% load so i turned on another 750 watt heater .. approx 30 seconds later, lights dimmed slightly, Zantrek panel (Zantrek 3000) jumped back from "AC on" to "inverter' and the "low Battery" indicator also came on.......Quickly turned all heaters off and microwave off .... turned off generator for a few minutes.... restarted generator but the Zantrec panel will not go back to "ac in'.....shut off the generator after a few minutes...
Could this be as simple as maybe a circuit breaker switch popped on the generator or other ideas?
Getting out the manuals....
 
WOW .. Talk about getting lucky and having Didalot_rv a few coaches away in same campground area ...
Checked out everything and he got it going in just a few minutes...
Turns out that I was only at 60-70% load on the gen in total - all the heaters and the microwave were in separate outlets - but all on the passenger side.... two breakers inside the coach (under the refrig) had tripped....
Reset those and all's well..... if it wasn't midnight (almost), I should run to town and pick up a lottery ticket.
Huge Thanks Mark...
I owe you one .. or two...
WhiteEagle
 