A member with a 2015 Forest River Forester MBS questioned whether an older PD9260C converter was failing because it stayed around 13.6V to 13.8V on shore power, did not show the expected 14.4V boost when first plugged in, and did not appear to drop to about 13.2V storage mode during winter storage. Several members said 13.6V to 13.8V can be normal when batteries are already charged, suggested verifying measurements with the battery rested and disconnected, and noted that the converter may...
More...
A member with a 2015 Forest River Forester MBS questioned whether an older PD9260C converter was failing because it stayed around 13.6V to 13.8V on shore power, did not show the expected 14.4V boost when first plugged in, and did not appear to drop to about 13.2V storage mode during winter storage. Several members said 13.6V to 13.8V can be normal when batteries are already charged, suggested verifying measurements with the battery rested and disconnected, and noted that the converter may not enter boost unless the batteries are discharged enough or the charge cycle is reset.
The original poster later measured about 13.38V after two days on shore power and reported that Progressive Dynamics support said the PD9260C should enter storage mode after about 36 hours with no loads, but that staying in normal mode should not harm the AGM batteries. Members also discussed possible differences between shore power and generator behavior, including AC input voltage, transfer switch interruption, Charge Wizard operation, AGM resting voltage, and checking output fuses. The topic did not prove the converter had failed, and the practical outcome was to keep monitoring it, compare behavior on a campground 30 amp hookup, and have the service shop verify startup charging mode.