I've investigated here and elsewhere the possibility of running my 13500 BTU air conditioner using a single Honda 2200i generator. Most reports recommended using a hard-start capacitor which I don't currently have. I thought I'd just give it a try and to my surprise the compressor kicked on, though it did take around 5 seconds, and started cooling without the generator overload light coming on.
The generator specs are marginal for this A/C but are within limits:
* Honda 2200i, 2200W starting, 1800W running
* Dometic Airxcel 48253c969 (aka Mach 3), 13500 BTU,1650W-1900W depending on conditions.
In case these A/C details makes sense to anyone:
1650W - Cooling A.R.I. Standard Conditioning 80? F.DB/67? F.WB Indoor, 95? F.DB Outdoor at 115VAC
1900W - Cooling A.R.I. Standard Conditioning 95? F.DB/71? F.WB Indoor, 115? F.DB Outdoor at 103.5VAC
When needed, I plan to run the A/C only at night so outside temperature is assumed to be 80F or below. Assume all appliances are off, including refrigerator on gas, and battery fully charged (so no power converter draw).
My question is - if there is a repeated overload condition will this hurt either the generator or the A/C compressor, or will it just not cool?
The generator specs are marginal for this A/C but are within limits:
* Honda 2200i, 2200W starting, 1800W running
* Dometic Airxcel 48253c969 (aka Mach 3), 13500 BTU,1650W-1900W depending on conditions.
In case these A/C details makes sense to anyone:
1650W - Cooling A.R.I. Standard Conditioning 80? F.DB/67? F.WB Indoor, 95? F.DB Outdoor at 115VAC
1900W - Cooling A.R.I. Standard Conditioning 95? F.DB/71? F.WB Indoor, 115? F.DB Outdoor at 103.5VAC
When needed, I plan to run the A/C only at night so outside temperature is assumed to be 80F or below. Assume all appliances are off, including refrigerator on gas, and battery fully charged (so no power converter draw).
My question is - if there is a repeated overload condition will this hurt either the generator or the A/C compressor, or will it just not cool?