Power=Voltatge X Current. (W=E-I)
Therefore, Power/Voltage=Current (W/E=I)
1800 Watts/120 Volts = 15 amps.
NEC requires that breakers only be loaded ,for continuous draw, to 80% of their capacity. For a 15 amp breaker that means they should only be presented with a maximum continuous load of 12 amps - therefore any 1800 watt load is WRONG on a 15 amp breaker is wrong.
With a 20 amp breaker, the max continuous load, per NEC guidelines, would be 16 amps. Therefore, OP's present oven AND the new oven require a 20 amp breaker to fall within NEC rules.
Follow
@OldWEB - install a proper
20 dedicated breaker. And do not share that breaker with any other device or you will push it over the NEC limit.