Here's a long one, but I think it's worth reading, because it applies to a lot of us. See if you can figure out what caused this problem before I tell you.
Cyndi and I had promised our 6 year old grand daughter that we'd take her camping - just the three of us, so off we went this weekend to a local County campground. Once there, I plugged our Progressive portable surge guard unit into the 50 amp power pedestal, as I've done countless times. I waited for it to indicate that the power was OK, and to transfer power to the coach. When it did, I went inside to the One-Place panel and turned on the two front AC units.
There was the normal 30 second delay (or so) and then the two forward AC units kicked on. I was about to start some other tasks when I noticed that the Magnum inverter's remote had a "High ACV" error message and a warning light, and the inverter had shut itself off. "Huh?" First time I'd ever seen that.
Then a loud, rapid clicking noise started up in the rear bathroom. It was the washing machine's electric door latch, locking and unlocking on its own - about once every half second. The odd thing was, the washing machine's power was off, and the On/Off switch wasn't responding. Then, "Bang!" The clicking noise stopped and I could see a small flame lapping up from under the washer's tumbler. Uh oh!
I yanked the washer and dryer's power cords out of their sockets, then rapidly moved to the foot of the bed to manually trip their circuit breakers and get a nearby fire extinguisher. (The breakers hadn't tripped on their own.) As I was doing so, I saw smoke coming out of the AC roof air ducts, so I tripped their breakers too. The flames in the washing machine went out on their own after about 10 seconds.
I thought, "What the hell is going on!" I turned on the roof vents to dissipate the acrid odor and smoke (it smelled electrical) and I told Cyndi and Jo Jo (our grand daughter) to stay outside while I troubleshot.
I re-checked the Progressive surge guard, and it still indicated that all was well - 119 volts on each line and no errors. Stumped, I disconnected from shore power, visually checked the transfer switch to verify that there were no obvious problems (burn marks, smoke, odors etc.) and there were none. I checked the Magnum remote again, and the high voltage warning message was gone.
I started the generator and it powered everything just fine - with no inverter error messages. (I didn't check the washer - I knew it was toast.) All three AC units worked, and there was no more smoke coming from the vents.
I started to focus on the Progressive surge guard, thinking it was somehow malfunctioning and letting bad power into the coach. As a simple test, I disconnected the surge guard and plugged the power cord directly into the power pedestal. Everything in the coach worked fine. To confirm my suspicion that the surge guard was malfunctioning, I plugged the power cord back into the surge guard and discovered that I now had power to some circuits in the coach, but not to everything, and there were no high voltage error messages. That made no sense to me.
Then it struck me... there's one component that could cause these problems - the power cord plug. I disassembled it and sure enough, the white wire was loose. There were indications of significant arcing and there were burn marks on other wires. It was a Camco plug and I installed it about four years ago.
I'm no electrician, but it appears to me that, somehow, the loose wire was shorting out and causing 240 volts to get to the coach. That's the only thing I can think of that would cause the Magnum inverter's high voltage error message and its automatic shut-down. It would also explain the electrical overload of the washing machine and the smoke from the AC ducts. After removing all the covers from the AC units, I found that the armature on one of the condensation water pumps had burned up. Apparently, that's what caused the smoke.
If someone's got a better explanation, I'm all ears.
So in the end, my portable Progressive surge guard was working fine, but I assumed it would prevent all electrical problems from getting to the coach. The truth is, portable units only prevent some electrical problems from getting to the coach. A downstream short circuit - even as close as the adjascent power cord plug (a $30.00 part) can wreak havoc. I'm replacing my portable unit with a permanently mounted unit - installed downstream from the power cord plug. It would have detected the high voltage problem and not allowed power to flow to the coach. It would have been a real shame if that fire had gotten out of control and destroyed the coach.
Kev
Cyndi and I had promised our 6 year old grand daughter that we'd take her camping - just the three of us, so off we went this weekend to a local County campground. Once there, I plugged our Progressive portable surge guard unit into the 50 amp power pedestal, as I've done countless times. I waited for it to indicate that the power was OK, and to transfer power to the coach. When it did, I went inside to the One-Place panel and turned on the two front AC units.
There was the normal 30 second delay (or so) and then the two forward AC units kicked on. I was about to start some other tasks when I noticed that the Magnum inverter's remote had a "High ACV" error message and a warning light, and the inverter had shut itself off. "Huh?" First time I'd ever seen that.
Then a loud, rapid clicking noise started up in the rear bathroom. It was the washing machine's electric door latch, locking and unlocking on its own - about once every half second. The odd thing was, the washing machine's power was off, and the On/Off switch wasn't responding. Then, "Bang!" The clicking noise stopped and I could see a small flame lapping up from under the washer's tumbler. Uh oh!
I yanked the washer and dryer's power cords out of their sockets, then rapidly moved to the foot of the bed to manually trip their circuit breakers and get a nearby fire extinguisher. (The breakers hadn't tripped on their own.) As I was doing so, I saw smoke coming out of the AC roof air ducts, so I tripped their breakers too. The flames in the washing machine went out on their own after about 10 seconds.
I thought, "What the hell is going on!" I turned on the roof vents to dissipate the acrid odor and smoke (it smelled electrical) and I told Cyndi and Jo Jo (our grand daughter) to stay outside while I troubleshot.
I re-checked the Progressive surge guard, and it still indicated that all was well - 119 volts on each line and no errors. Stumped, I disconnected from shore power, visually checked the transfer switch to verify that there were no obvious problems (burn marks, smoke, odors etc.) and there were none. I checked the Magnum remote again, and the high voltage warning message was gone.
I started the generator and it powered everything just fine - with no inverter error messages. (I didn't check the washer - I knew it was toast.) All three AC units worked, and there was no more smoke coming from the vents.
I started to focus on the Progressive surge guard, thinking it was somehow malfunctioning and letting bad power into the coach. As a simple test, I disconnected the surge guard and plugged the power cord directly into the power pedestal. Everything in the coach worked fine. To confirm my suspicion that the surge guard was malfunctioning, I plugged the power cord back into the surge guard and discovered that I now had power to some circuits in the coach, but not to everything, and there were no high voltage error messages. That made no sense to me.
Then it struck me... there's one component that could cause these problems - the power cord plug. I disassembled it and sure enough, the white wire was loose. There were indications of significant arcing and there were burn marks on other wires. It was a Camco plug and I installed it about four years ago.
I'm no electrician, but it appears to me that, somehow, the loose wire was shorting out and causing 240 volts to get to the coach. That's the only thing I can think of that would cause the Magnum inverter's high voltage error message and its automatic shut-down. It would also explain the electrical overload of the washing machine and the smoke from the AC ducts. After removing all the covers from the AC units, I found that the armature on one of the condensation water pumps had burned up. Apparently, that's what caused the smoke.
If someone's got a better explanation, I'm all ears.
So in the end, my portable Progressive surge guard was working fine, but I assumed it would prevent all electrical problems from getting to the coach. The truth is, portable units only prevent some electrical problems from getting to the coach. A downstream short circuit - even as close as the adjascent power cord plug (a $30.00 part) can wreak havoc. I'm replacing my portable unit with a permanently mounted unit - installed downstream from the power cord plug. It would have detected the high voltage problem and not allowed power to flow to the coach. It would have been a real shame if that fire had gotten out of control and destroyed the coach.
Kev