Heck GFCIs don't play well when another GFCI is downstream from them...
Done that many times. NEVER a problem. Not once.
Heck GFCIs don't play well when another GFCI is downstream from them...
I'm glad to hear you've not had any issues.Done that many times. NEVER a problem. Not once.
It's my understanding that the more recent levels of the NEC do require GFCI for newly installed 30A/120v outlets. I've read reports that COE parks are getting their 30A outlets upgraded.For that reason, the NEC does not require that the 30A or 50A outlets for an RV be GFCI protected.
What I found is that beginning in 2026 the NEC will require Ground Monitoring Interrupters on RV pedestal 30A and 50A outlets. But those are quite different from the present GFCI. Here is what I find by way of the difference:It's my understanding that the more recent levels of the NEC do require GFCI for newly installed 30A/120v outlets.
Here's what I can tell you as an absolute. I have seen it in my years of wiring residentially and industrially. GFIs don't stack well line to load. Most times it works fine and sometimes it doesn't. Some particular inductive loads will trip a GFI. Every now and again one will do it but most do not. I suppose some inductive loads at some point in the startup process don't exhibit balanced line and neutral for some short time period. GFI receptacles are more prone to nuisance trips that a quality GFI breaker. Not all but some. My fridge on my RV does it. One of my freezers in my garage does it. I don't use GFI receptacles anywhere after losing a freezer full of meats and vegetables to one. But, breakers are much more expensive.In my experience the only "nuisance" with series GFCI is that when one GFCI trips, they all trip. That's by design.
There is no reason for a GFCI to ever pass current to the ground instead of neutral, even during a self-test or reset. In fact, a GFCI is supposed to function properly without a ground wire present at all. And as long as the downstream GFCI passes a test current only to the neutral side, it cannot "confuse" the upstream GFCI. Whatever it does, it's just another load.
I see no reason an inductive load is any different from the GFCI perspective. Whatever the load is, it's just some amount of amps in the wire. If the difference between hot & neutral exceeds 6 ma, the GFCI trips.
However, some loads are more prone to producing ground faults than others, leaking a few milli-amps to ground. Motors (classic inductive load) are an example. Removing the GFCI gets rid of the nuisance, but doesn't get rid of the current leakage problem. You just have to hope the amp leakage never gets high enough to be really dangerous.
Right, GMI is an entirely different function than GFCI. The only thing they have in common is the word "ground".What I found is that beginning in 2026 the NEC will require Ground Monitoring Interrupters on RV pedestal 30A and 50A outlets. But those are quite different from the present GFCI. Here is what I find by way of the difference:
A Ground Monitor Interrupter (GMI) works by continuously checking the integrity of the earth (ground) connection in an electrical system, often in applications like RVs or EV chargers. Unlike a GFCI which monitors current flow for imbalances, a GMI specifically tests if there is a valid, low-impedance ground path. If the GMI detects a high-resistance or missing ground connection, it will prevent power from being supplied to the device or disconnect it from the power source, ensuring safety by preventing a dangerous "hot skin" condition.