Using a separate 20 amp cord to the pedestal will work. Don't go cheap on the extension cord - a contractor grade 12 gauge cord is much better than one with 14 or 16 gauge wire (lower numbers = thicker wire) since you'll be running it at close to it's capacity for long periods of time. And thin wire will reduce the voltage getting to the heater, reducing it's output.
In my rig, I added a dedicated outlet for the heater, using a quality home style outlet and box. It wasn't hard since my breaker box was centrally located and I could put the outlet close by, so it was easy to run the wiring. If your main 30 amp breaker is full width you can replace it with a 30/20 amp dual breaker to get the extra circuit. In my case, my box was already full of dual breakers, so I doubled up on the air conditioner's 20 amp breaker. If I'm dumb enough to run the a/c and heater simultaneously I deserve to have the breaker trip.
In my rig, I added a dedicated outlet for the heater, using a quality home style outlet and box. It wasn't hard since my breaker box was centrally located and I could put the outlet close by, so it was easy to run the wiring. If your main 30 amp breaker is full width you can replace it with a 30/20 amp dual breaker to get the extra circuit. In my case, my box was already full of dual breakers, so I doubled up on the air conditioner's 20 amp breaker. If I'm dumb enough to run the a/c and heater simultaneously I deserve to have the breaker trip.