I was having a problem melting the male end on my power cord in a spot I was using all summer, Also had a AC lights flickering (DC was ok). I pulled the cover off the pedastal and found that the hot lead on the 30amp plug had had a crimp on round eyelet under the screw, the eyelet was so burnt that only about 3/8 " was left holding the wire to the screw. I took the wire loose, cut it back to clean/bright copper, and refastened the wire. Problem was solved.
I would have the maintance man pull the cover and check the connections. Older parks don't always check there pedistals like they should.