Is 240v / 50a supply the standard for new TT's in the say 24' and larger class or is it still more dependent on "as equipped" ?
Are some still 120/30 ?
Are some still 120/30 ?
The simple answer is no, it is not standard. That said there are manufacturers that put 50A service in as standard on some models. In most cases it will depend on the particular model and will be more common in the higher priced models. It is much more common when there are 2 air conditioners but even then is not always standard but may be an option. I don't believe that there is anything that is an industry wide standard but 50A service is usually available in larger and more expensive models.Is 240v / 50a supply the standard for new TT's in the say 24' and larger class
240 VAC is rarely used even with 50-amp service.Is 240v / 50a supply the standard for new TT's in the say 24' and larger class or is it still more dependent on "as equipped" ?
Sorry, it has to be 240V for the 50A service. 240V is never(?) used but is required if you expect to load up the two 120V lines to 50A each.240 VAC is rarely used even with 50-amp service.
It's usually two lines of 120 VAC that are used, 50 amps each, for a total capacity of 100 amps at 120 VAC.
-Don- Reno, NV
240 VAC is rarely used even with 50-amp service.
It's usually two lines of 120 VAC that are used, 50 amps each, for a total capacity of 100 amps at 120 VAC.
-Don- Reno, NV
Well that's just wrong.240 VAC is rarely used even with 50-amp service.
It's usually two lines of 120 VAC that are used, 50 amps each, for a total capacity of 100 amps at 120 VAC.
-Don- Reno, NV
I beg to differ. The vast majority of RV's built in the last 25 years are called "50A service". Actually there are 2 legs of incoming 50A service in a 120V configuration inside the RV main panel, for a total of 100A available @ 120VAC. A few high-end MH's actually are wired for 100A service @ 240VAC, they are all-electric MH's.Ordinarily if it’s equipped with two a/c’s it’s going to be 50A 240V, in some cases a unit with two a/c’s may be 30A 120V with a power management/ load shedding system. If it’s wired for a second a/c it may well be 50A already. However, a 30 A with one 15k btu a/c w/o a special capacitor is not going to let you run the a/c with a blow dryer or the microwave at the same time, regardless what the salesman says.
Not exactly. The 2 50A legs in the 120VAC main panel configuration requires the neutral to carry some current.No it's not supposed to be what you describe puts 100 amp on the neutral wire
It's supposed to be 240 volt center tap (Divided) so that .. Ideally. the neutral crarries nothing. or nearly nothing.. This is the precise same service (Other than the size (50 amp 100 150 200 more) you have in your house. Not sure what I have in my apartment (no main breaker it's elsewhere) but it's 240 volt.. Divided. But it's truly 240 volt at 50 amp. that's why they call it 50 amp.
Some parks do.. however.. Cheat (or so I'm told and put in the same leg to both sides.. That's a fire hazard.
The neutral is called that because it is the center-tap of a 240 VAC home transformer. It does nothing at all on a 240 VAC circuit... Ideally. the neutral crarries nothing. o
The following is a write up that I did a while back to help explain the RV 50A Electrical system. Many times, there is a discussion about this topic, and consequently, a lot of information that is given is not correct and only serves to further confuse people. So, hopefully this will help and feel free to use it as a reference.
I have to admit....I'm still in shock (no pun intended) at some of the outrageous and totally wrong comments/info that have been given on this topic. The RV electrical systems have been engineered by professional folks, following an established method of electrical distribution that is not subject to your opinion or what you think on how it "should" work, it's based on how it DOES work. So in this case, opinion is totally irrelevant.....and FACT is the determining method of RV electrical systems. The following is a brief explanation of RV 50A Electrical Service….
And the facts are this! A 50A RV electrical system will be comprised of two hot legs, created by what is known as a Split Phase system, and thought of as L1 and L2, a neutral wire, and a ground wire. The two hot legs will be 180 degrees out of phase with each other (and if you don't know what that means, you likely are not going to thoroughly understand how it works) and they WILL IN FACT be able to provide 50 amps of 120VAC PER LEG. In the case of a 50A RV Electrical system, it is basically the exact same as the electrical distribution system INTO your house or home. The difference between the two (RV and your house) is in the electrical distribution panel....a.k.a. the breaker panel. Up to that point (disregarding that fact that your house will use a ground rod at the service entrance and your RV has a continuous ground wire from the pedestal to your RV) the two are exactly alike. Distribution of that power is where the difference is...not the power source itself.
The RV breaker panel is made so that the 50A Main breaker is located in the center of the panel and the associated bus work for each hot leg goes in opposite directions, so it is impossible to have a 240VAC circuit Safely and within Code specs, any place other than the Main breaker itself. In regard to the 50A Main breaker....the LEFT (or top) most half of that breaker feeds 120VAC (with respect to neutral) only to the LEFT (or top) side of the panel for the purpose of being able to install single pole breakers into the available spaces on the LEFT (or top) side of the panel. The RIGHT (or bottom) most half of the 50A Main breaker feeds the bus on the RIGHT (or bottom) side of the panel, providing 120VAC (with respect to the neutral wire) to all of the available slots on the RIGHT (or bottom) side of the panel. The left (or top) side of the panel can be thought of as Phase A...or L1.....and the right (or bottom) side of the panel would then be Phase B... or L2....and MOST IMPORTANTLY....L1 and L2 are electrically 180 degrees OUT OF PHASE with each other. The fact that the two hot legs are 180 degrees out of phase with each other, is what allows the neutral wire to NEVER have to carry any more than 50 amps of current.....even if each leg is pulling the maximum amount of current available to each leg.....50 amps each. So Yes, there is 240VAC coming into the trailer 50A panel, just like there is 240VAC coming into your house. But again, the house breaker panel and the RV breaker panel are configured differently and the result is that you do NOT have 240VAC available for circuits in the RV panel….because of the separation of the two buss bars in opposite directions.
It's really pretty simple if you have been trained and or have knowledge of how a split phase electrical distribution system works.....if you don't, it might be a bit troublesome and cause you to make statements that may not be true at all. Sorry for the long-winded post, but hopefully it may help clear up some of the mis-statements made in this ongoing topic. "
I think you mean 50 amps at 240 VAC. That is 12,000 watts already.A few high-end MH's actually are wired for 100A service @ 240VAC, t
You made the same mistake again. That would be 24,000 watts. A 14-50R is only good for 50-amps/240 VAC. The amp rating is what the "50" means in 14-50R or 14-50P.In actuality it is a total of 100A@ 240VAC
A house can be wired for more than that, but the 14-50R at RV parks are only rated for 50 amps at 240 VAC. If an RV park is going to change to 100-amps at 240 VAC, what will be used for the outlets?my house has 100A 240VAC
Yep. The main part we were discussing here was:Post #13 is exactly what I would expect in a 50A supply RV
Not exactly. The 2 50A legs in the 120VAC main panel configuration requires the neutral to carry some current.
Most 50A RV main panels are designed so installing a 240V breaker is impossible. The 4-wire "50A" RV park pedestal is wired exactly like a 100A 240V 4-prong receptacle.
Don is right.