I am out on a month long trip and our refrigerator has stopped working, Dometic RM1350. I have downloaded the service manual and gone thru the troubleshooting steps and believe the cooling unit may be dead, but have a couple unanswered questions?
The boiler gets hot on BOTH propane and electric but the coils no longer heat up.
Can the control board cause this? or does the control board ONLY control the boiler operation?
There is no apparent leak in the cooling unit, no odor whatsoever ( I have had one go out on another rv and it clearly smelled of ammonia).
The thermistor checks out as it should with an ohmeter both in icewater (9100 ohm) and ambient (5000 ohms)
all control buttons and digital display working properly
Unit is 2009 and has always maintained 34 f tremp. Problem started out as intermittent, would stay at 34 f for days then spike to upper fortys and fiftys and then cool back down to 34 for a couple days and then spike again and eventually stopped cooling altogether even though boiler gets hot
This just seems like a control issue rather than the cooling unit and I would hate to replace the cooling unit only to find out it still doesn't work
Any help or insight would be greatly appreciated, please feel free to email me as well as post a reply. Right now we are using a small (very small) electric fridge for basics.
I am out on a month long trip and our refrigerator has stopped working, Dometic RM1350. I have downloaded the service manual and gone thru the troubleshooting steps and believe the cooling unit may be dead, but have a couple unanswered questions?
The boiler gets hot on BOTH propane and electric but the coils no longer heat up.
Can the control board cause this? or does the control board ONLY control the boiler operation?
There is no apparent leak in the cooling unit, no odor whatsoever ( I have had one go out on another rv and it clearly smelled of ammonia).
The thermistor checks out as it should with an ohmeter both in icewater (9100 ohm) and ambient (5000 ohms)
all control buttons and digital display working properly
Unit is 2009 and has always maintained 34 f tremp. Problem started out as intermittent, would stay at 34 f for days then spike to upper fortys and fiftys and then cool back down to 34 for a couple days and then spike again and eventually stopped cooling altogether even though boiler gets hot
This just seems like a control issue rather than the cooling unit and I would hate to replace the cooling unit only to find out it still doesn't work
Any help or insight would be greatly appreciated, please feel free to email me as well as post a reply. Right now we are using a small (very small) electric fridge for basics.