JoelP said:
Thanks Solarman for your reply. I now have two 6 volt Deka batteries that are each labeled :75Amp rating 120 min. I would assume that this means they could together deliver 75W for 240 minutes when in optimum condition. In your nomenclaturee it would seem to me that these are 150 amp hr batteries, and together these to could deliver 300 amp hours. 1% would be 3 amps and 2% 6 amps. 6 amps at 12 volts would mean 72 watts. Am I figuring this right? I would then need 75 -100watt system. How much would that run me? Am I figuring this right?
BTW I installed these 6 volt batteries this afternoon and they basically work, but I have some questions. I asjed the shop that sold them to me if they were already charged and was assured that they were. And yet, when I checked them, they were only at 37% charge level. Is that typical? If so how can a dealer store them for any period of time with <50% charge and not suffer degradation?
I ran my genset for a couple of hours and the level meter I have on this read 97% butit soon settled back to 45%. I know that it takes more than a couple of hours to charge batteries. I also measured them with a hydrometer and they showed a level of just between fair and good, no doubt due to the lack of full charge
Let me add that I very much appreciate the time that so many have spent to answer my questions on batteries. I have learned a great deal. It was good to go back and read that library article on batteries. While i had read this last year, not all of it was retained..
For capacity it is normal to specify the 20 hour rate, Larry has posted a table of capacity vs discharge rate.
GC2's are nominally 200 to 230 Ah @ 20 hr rate depending on manufacturer.
you are confusing Amps and Watts..
for SERIES connection, VOLTAGE is the sum of all battery voltages and AMP Hours is that of one battery
for PARALLEL connection, VOLTAGE is of one battery and AMP Hours are the sum of all batteries
so for your 6 Volt batteries we have 6 Volts and 200 Ah, therefore in series you have 12 Volts and 200 Ah.
1% of 200 Ah is 2 Amps. for maintenance purposes I would suggest a 50 Watt panel.
Batteries when new may be stored for quite some time on the shelf in an inactive state.
the manufacturer fills the battery with acid of the correct SG so it's effectively fully charged.
as no charging current has been applied, the "destructive" chemical reactions have not yet taken place
and will not effect the life for at least 6 or 8 months.
A new "off the shelf" battery should be fully charged and also given and equalization charge before use ( ideally ).
also, don't expect the battery to give full capacity right away, it usually takes at least 10 cycles before the capacity
comes up to spec..
Note that i'm assuming you have wet cells, if your batteries are AGM then do NOT apply an equalizing charge.