Furnace was working great. Fan comes on and it doesn't even stay on long enough to try to ignite and shuts down. Have to pull the unit to check the sail switch unless someone has some advice.
I would not think that would cause any problems unless something pretty unusual happened. If the frunace was off at the thermostat at the time or if on but not calling for heat, there would have been no power to the furnace circut board. To totally isolate it you would need to remove the fuse that supplies it. If you disconnedted the negative battery post first and reconnected it last, there is almost no chance that you damaged anything.I think I may have tweaked the system by changing one of my battery connections to a wing nut and forgot to turn of furnace.
The manual link that Kirk seems a little dated,
When the propane ignites, does the ignition probe stop sparking? If it doesn't then it isn't detecting the heat from the burning propane. If it does burn for a full minute, that is longer than would normally be the case with a sensing failure but you may still want to consider that probe. At least try cleaning and tightening the connection to the probe as the sensing signal is in the micro-volt range and can easily be lost.Checked the high temp limit switch and it is working fine, and even out a jumper to bypass it and the same thing happens... it shuts down after about a minute of working fine.
Yes, it does stop clicking by the way. It starts clicking again as soon as I hear the flame go out, but does not light again as it must shut the gas valve down or something.View attachment 161828
When the propane ignites, does the ignition probe stop sparking? If it doesn't then it isn't detecting the heat from the burning propane. If it does burn for a full minute, that is longer than would normally be the case with a sensing failure but you may still want to consider that probe. At least try cleaning and tightening the connection to the probe as the sensing signal is in the micro-volt range and can easily be lost.
I just noticed that link that I sent didn't work so use this one instead.It starts clicking again as soon as I hear the flame go out, but does not light again as it must shut the gas valve down or something.
That is a clear indication that the system did lose the return signal from the ignition probe and that it was due to the flame going out. The most probable reason that I can think of would be a loss of propane supply. If I am right that would leave 2 prime suspects, the supply valve or the propane regulator. As a next test, I would light a burner on the stovetop and let it burn for several minutes, then with it still burning start the furnace and see if the symptoms remain the same and what that burner's flame does at the same time. If the regulator is the problem it should show in the stovetop burner's flame as well, if the furnace lights at all.t immediately attempts to relight by the clicking of the ignitor, but after the 3 attempts it stops and the motor runs the shutdown cycle.
My guess is that there is a problem with the air+gas mix, which usually means either an impediment in the exhaust or air intake tubes or a leak in the gaskets around them. Most people think LP gas as highly explosive, but in fact it is extremely fussy about having an exact air/fuel mixture for combustion. Rust flakes, insect webs or nests, or anything that disrupts the pre-tuned in/out flow can cause the burner to flame-out. And be unable to re-light.I go out by the exhaust to listen and feel the flame go out. You can tell by the sound and by the moisture change in the exhaust. It immediately attempts to relight by the clicking of the ignitor, but after the 3 attempts it stops and the motor runs the shutdown cycle.