Works fine in AC mode. Fires and runs for 30 seconds or so and trips off, with the "check" light illuminated. I can reset it and if fires again but trips off.......
same symptoms whether plugged into shore power or not....
so, when it fires it has a good blue flame, and my voltages are good. the thermocouple was quite dirty so I used a tiny wire brush on that, no change.
after reading a bunch of older threads, I'll try cleaning the terminal connections at the control board, but I've unplugged and replugged the t/couple wires a few times so I don't think that is the problem......
I did test the t/couple for resistance, it's open until it gets warm (10 seconds or so upon start up) then ohms climb pretty fast......should I be checking for millivolts instead?
I guess I'll start with a new thermocouple.........it's the least expensive part. I've located a control board so I will get that if the new t/couple doesn't fix it.
am I missing something simple?
thanks in advance for any suggestions!
same symptoms whether plugged into shore power or not....
so, when it fires it has a good blue flame, and my voltages are good. the thermocouple was quite dirty so I used a tiny wire brush on that, no change.
after reading a bunch of older threads, I'll try cleaning the terminal connections at the control board, but I've unplugged and replugged the t/couple wires a few times so I don't think that is the problem......
I did test the t/couple for resistance, it's open until it gets warm (10 seconds or so upon start up) then ohms climb pretty fast......should I be checking for millivolts instead?
I guess I'll start with a new thermocouple.........it's the least expensive part. I've located a control board so I will get that if the new t/couple doesn't fix it.
am I missing something simple?
thanks in advance for any suggestions!